Thanks for the answer.

That is what we were suspecting.

Online searches found no good usable data so we ask here as others likely been there.

Spent many years managing vrla or Agm battery plants for telecom switches and communications sites so very well versed in the charging and use of this type of battery.

The ones we have are cycle service for ups type loads where high currents both charge and discharge are expected instead of the common float service ones common to cell sites and switches.

The charger works fine and does not exceed rate of charge but the end voltage being too high causes battery to be in equalize mode when it should be fully charged and either charger off or floating.

Float charge should not exceed 0.1% C where C =120 (cannot remember exact ah today) so float charge should not exceed 0.12 amps.


Also of minor note is fully charged in generic terms 2.25 VPC is considered fully charged, this would be 40.5 VDC total.
Each battery model has specific voltage but generic value can be close enough for general discussion.

Charging above that point for short periods will attempt to equalize the battery plant but most VRLA/AGM batteries will void warranty if equalized.

Charger is still at 5 amps when it should be fully charged so for short term we will need to manually control it.

Was looking at tinkering with the pot to cause the charger to turn off at lower voltage or we may just build something.
Quote:
Originally Posted by JohnnieB View Post
The Powerwise 28115 charger is a ferroresonant transformer type charger and its charge profile is based on the attached recommendations from Trojan Battery for their Lead-Acid Deep-cycle Wet-Cell batteries.

Basically, it starts out in a constant current mode (18A - 20A) until the on-charge voltage climbs to about 42V and then the amps start decreasing as the on-charge voltage increases. As the amps decrease to about 5A as the on-charge voltage approaches about 45V and the charger shuts off.

The max recommended charging amps for AGM is roughly 1/2 of what the max recommended charging amps for a wet-cell is and the 120AH batteries are roughly 1/2 the capacity of the 225AH wet-cell batteries the PW 28115 is designed to charge, so the initial amps (constant current mode) will be about 4X what your 120AH batteries can tolerate.

Also, the max recommend finish voltage for a 36V AGM battery pack is 44.1V and the PW 28115 shuts off at 45V +/-1V. However, you might be able to lower this to 44V or less by adjusting the pot on the control board. Of course, the AGM batteries will probable be cooked before the on-charge voltage gets that high due to the 4X higher than recommend amps.

Pages 19 and 20 of attached Trojan Battery user's guide have the charging profiles for Wet and AGM batteries.